FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

G3.1.10 (d) "Heating only System"

Based upon G3.1.10 (d) “Where no cooling system exists or no cooling system has been specified, the cooling system shall be identical to the system modeled in the baseline building” Does this means both Proposed and Baseline case should have same airflow and Fan power as calculated from baseline case? Could anyone please elaborate. Thank you Anil

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 02/27/2015 - 14:40

This for spaces that are heating only in proposed case. In baseline, you need to use system 10 or 11 for those heating only space. You only needs to match the OA (Typically is zero since heating only spaces usually are not occupied). Fan power is calculated based on 0.3 W/cfm as in system 1 fan power.

Fri, 02/27/2015 - 14:50

In the case where you do not have a system design or it is not a heating only system, you would model the same system type in both models but capacities, air flow, etc. may vary when they are auto-sized.

Fri, 02/27/2015 - 14:59

Thanks Marcus, My system do not fall under system 9 or 10. Its a dormitories with heating and ventilation. Baseline heating and cooling capacities are auto-sized based upon G3.1.2.2 and Fan power based upon G3.1.2.9. For proposed case shall if i use auto-sized air flow and fan power based upon G3.1.2.9. Than air-flow and fan power data will be different from actual unit installed. Ultimately it will show inconsistent between data input in table 1.4 and mechanical schedule . Any though? Thanks you Anil

Fri, 02/27/2015 - 15:37

Rather than even mess around with this requirement for having to model a non-existing system I would tell the reviewer in a narrative that you can model the cooling systems but if you did you would increase the temperature set point so that it never came on. The ability to adjust the set point really negates the need to model a system that does not exist so it becomes a waste of time to model it.

Fri, 02/27/2015 - 16:13

It mean we need to model Proposed case air flow and fan power (kw) as installed not the one calculated from baseline case? Thanks Anil

Fri, 02/27/2015 - 21:51

You almost always model the proposed as designed.