Forum discussion

NC-2009 IEQp1:Minimum IAQ Performance

Fresh air fan model

Hi We are working on a Data center LEED project. Do we need to model the fresh air fan for server room area because there were already exhaust fan and fire suppression system? Please clarify of this issue. Thank you, Regards

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/15/2017 - 01:16

Sivarajah, This depends on where your exhaust fan is pulling air from. If you get fresh air using and exhaust fan you do have ventilation for this space. The fire suppression systems is irrelevant to this credit in my opinion.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.