Free fresh air provided to small rooms

I am working on a project with many small buildings connected to each other , some of the very small rooms may be designed with free fresh air entering through fresh air grilles not fans , is this suffecient for this credit ?

 

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 10/25/2021 - 07:22

Hi Dina, if you are using wall openings covered with fins, you can only count free area and perform calculations based on either ASR, ASHRAE, or CIBSE Standards. Apart from that, ASHRAE offers the possibility to demonstrate compliance with an engineered natural ventilation system: https://www.usgbc.org/resources/verification-protocol-engineered-natural-ventilation-systems-equatorial-climates

Mon, 10/25/2021 - 14:08

Hi Dina, I wish to add based on the codes mentioned by Gustavo, basically you need to comply the followings:
- ASHRAE 62.1.2010 item 6.4.1 and 6.4.2
- CIBSE Figure 2.8 compliances
- To install CO2 sensor on each thermal block at human level with audible or blinking system when the level exceeds the set point  