NC-2009 MRp1:Storage and collection of recyclables

Form Template Compliance

We are working with a University that collects everything but Glass however that is detailed out in the special circumstances. Without checking the box marked for "Glass" in the form, it is not recognizing compliance. Does anyone know if we need to just mark it and rely on the explanation in the dialog box for reviewer documentation? Otherwise, it doesn't appear that we can check the status as "complete" in order to submit.....

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 03/30/2012 - 18:53

I think you have identified the correct process and necessary steps. Be sure your narrative is clear and mentions if co-mingled collection is occurring.

Fri, 03/08/2013 - 22:35

There was LEED Interpretation about this- #1803 "Given the location and infrastructure of your project,you will not be required to collect these materials that you cannot recycle. However, it should be noted that even if recycling does not exist [...] in the geographical area, space must be provided in the building in anticipation of recycling resources becoming available in the future. Please be sure to include a narrative with your submittal describing your recycling efforts[...]"