FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

fit out work

Part of my project is considered as fit out which means that there are some office floors where the area is divided into offices and to each office a chilled water tap point is provided is air conditioining and heating design is done but the tenant is expected to bring the a/c unit and to do his own duct distribution. my question is can I consider these areas as designed and assume one big fan coil serving each office?and how leed reviewer would considere it other wise

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 06/06/2012 - 09:32

IMO exactly correct. You must simulate the non-planned a/c units. Where no HVAC is defined, use the baseline systems...a baseline fancoil.

Wed, 06/06/2012 - 10:17

what did you mean by IMO, what did you mean by when no HVAC is defined? is fit out considered as core and shell or designed?

Wed, 06/06/2012 - 10:38

IMO = in my opinion In fact I will revise my previous comment. Since the HVAC is not defined here, I think the rules in Table G3.1 No. 8 should apply. Check the Table G3.1.1A&B to check what the baseline system type is. If, for example, your project requires system 7. for the baseline, then you could split off and define these spaces as seperate thermal blocks and supply them with the relevant baseline system which brings ventilation, cooling and heating.

Wed, 06/06/2012 - 10:51

let me rephrase your reply. 1- you considered a fit out as a core and shell. 2-The baseline should be as per appendix G table,but the spaces area will be very small so i will choose the smallest one. 3- I will consider each office (to which ine tap point s provided )as a zone. correct?

Wed, 06/06/2012 - 11:08

Good questions. 1. yes 2. no. the system type is considering the whole building as a whole, i.e. "where attributes make the building eligible for more than one baseline system type, use the predominant condition to determine the system type for the entire building." 3. not quite...you could just as always consolidate similar adjactent zones into one thermal block applying the rules of Table G3.1 No. 8...i.e. group offices that face the same direction and are next to each other.

Thu, 06/07/2012 - 21:43

2. Unless one or more of the exceptions to G3.1.1 apply. 3. Also pay attention to G3.1.1 as the baseline modeling of thermal blocks varies for different systems.