Share your comments on the first public comment draft of LEED v5 BD+C/ID+C: Energy and Atmosphere category on this forum. You can either reply to this thread or use the "Post a Question/Comment" button to start a new thread.
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Lyle Axelarris
Boston Architectural CollegeApril 3, 2024 - 6:29 pm
See my comments below (sorry, used the wrong account)
Lyle Axelarris
Boston Architectural CollegeApril 3, 2024 - 7:13 pm
See my comments below (sorry, used the wrong account)
Lyle Axelarris
Building Enclosure ConsultantBPL Enclosure
60 thumbs up
April 3, 2024 - 7:21 pm
Minimum Energy Efficiency - "Comply with ASHRAE 90.1-2019 with addendum cr." Does this mean ONLY addendum cr, or all addenda issues prior to, and inclusive of, addendum cr?
It seems odd to not include all ASHRAE addenda, as we are required to comply with all LEED Reference Guide addenda. There are corrections and improvements alway being made, specifically addendum av (thermal bridging) is a critical update to ASHRAE 90.1-2019
Lyle Axelarris
Building Enclosure ConsultantBPL Enclosure
60 thumbs up
April 3, 2024 - 7:21 pm
Enhanced Commissioning Option 1 is listed as 1-2 points. But under Option 1, Path 2 (BECx) is shown as 1-4 points. Is BECx worth 2 points or 4 points? Why is it a range - what determines if you get 1 point or 2 (or 4) points?
Ed Simpson
Commissioning ProviderTESTCOMM, LLC
1 thumbs up
April 4, 2024 - 11:24 am
Fundamental and Enhanced Commissioning
Fundamental commissioning requirements for the CFR and Colntinuing O&M plan- Note that recent reviews have kicked back the point if the manual and CFR is not written exactly as shown in the description, or if the TOC is not detailed exactly as shown in the prerequisite description. Local energy code may require different format that includes essentially the same information and project specifications often dictate information contained in the documents. It is absurd that two separate documents need to be produced to conform to LEED format. Recommend that language be added that if the information contained in the TOC or submitted manuals (additional documentation supporting special circumstances) is substantially compliant, that the points be awarded.
James Lee
2 thumbs up
April 22, 2024 - 12:30 am
EA Credit: Renewable Energy
Option 1. Renewable supply or procurement
The sentence, "A maximum of four points are awarded as the sum of points documented for Tier 1, Tier 2, and Tier 3 in Table 1 based on the percentage of total annual base building site energy use, where base building energy use is defined as the greater of the estimated site energy consumption from base building energy meters or 25% of the total predicted building energy use", is somewhat confusing. Is it possible to define the bold, italicized terms and offer an example to illustrate how the point system works?
Mark Terpstra
April 29, 2024 - 9:45 pm
Enhanced and Ongoing Commissioning && Reduce Peak Thermal Loads
The air leakage testing is required for Enhanced Commissinoing for Building Enclosure and it under Reduce Peak Thermal Loads under Option 1. Infiltration and balanced ventilation.
Is it meant to appear in two credits?
Mark Terpstra
April 29, 2024 - 9:48 pm
Will there be any guidance on the Energy Performance credits from LEED v4/v4.1 to LEED v5. Alberta Infrastructure's Technical Design Requirements have a requirement for new-build schools and offices to achieve 12 points under Optimize Energy Performance under LEED v4.1. Under Option 2. Energy Simulation, what would that equate two?