FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

CS-2009 EAp2:Minimum energy performance

Fan power calculations

I have a question regarding the pressure drop adjustments. We are doing energy modeling for a data center. The Data halls in the building have an array of CRAC units with EC plug fans (for air flow modulation). These units are 100% re-circulation units. Ventilation / Pressurization air is supplied in these rooms through a separate unit. For the baseline system, we are using a system type-8 (VAV system with PFB boxes). For this baseline system can we take a pressure credit - "Return and /or exhaust airflow control device" as the proposed system (CRAC) can modulate(control) the air flow. In our case since there is only one fan, it could be taken either as supply or return fan.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 06/10/2014 - 12:48

I don't think you can take the pressure credit in the Baseline. Since, CRAC units are single zone and generally, doesn't require return air controller.

Tue, 06/10/2014 - 13:36

Agreed. These units would not typically have an eligible control.