FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Fan Power and Fan Power Adjustment (FPA)

Greetings, In the project we are modeling, the following issues are still not quite clear for us and we'd appreciate any advice on the matter. Baseline system is 8. The Proposed AHU systems are with fully ducted supply, return and exhaust parts. Their AHUs are provided with filter F7 (MERV13), rotary heat recovery device (HRD) and sound attenuator on the supply side. The questions are: 1. By applying the PD adjustments as per table 6.5.3.1.B, should we take the fully ducted PDA only once or we should apply it twice - for supply and return. Also regarding HRD, should we apply the PDA for the supply and for the return side or only once. 2. Baseline system 8 has a fan power related to the PFBs. How to estimated these powers. All comments and advices are highly appreciated. Thanks

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 11/07/2016 - 14:54

1. The PDA is for fully ducted return so it only counts once. 2. See G3.1.3.14 So it sounds like you can claim a PDA for fully ducted return (0.5), MERV 13 filters (0.9), and sound attenuation (0.15). Keep in mind that you can only claim the fully ducted return PDA if 100% of the returns are ducted. If you have one transfer grill or plenum return then you can't claim it (see the Under's Manual). Also you can only claim a PDA for heat recovery if it is required in the Baseline according to G3.1.2.10. It does not matter if there is heat recovery in the Proposed system.

Tue, 11/08/2016 - 13:20

Marcus, thanks a lot for the reply. Could you please clear also what is understood by airflow control devices and in what situationthey it could be applied. Is this closing or adjusting dampers on the return side and in which place. I'm sorry, but without some more explanation, I could've missed or unproperly apply them. Thanks.

Tue, 11/08/2016 - 15:21

That refers to situations only where the airflow is modulated to maintain relative negative or positive space pressure (e.g. lab, operating room). There may be a few other applications but this is rarely installed in most standard HVAC systems. The User's Manual has a good discussion of this I think. This one is often incorrectly applied.

Tue, 11/08/2016 - 15:25

Thanks a lot Marcus, I'd like to ask again about System 8 and the fan power assigned to fan powered VAV boxes - how to estimate it. Thanks.

Tue, 11/08/2016 - 15:42

ASHRAE 90.1-2007 Appendix G3.1.3.14 tells you how to model these boxes in the Baseline for a System #8.

Tue, 11/08/2016 - 15:48

Thanks Marcus, Sorry for didn't check about it. I do applogize

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.