FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Factory with a high unregulated energy loads- LEED EAp2

Hello, I am a beginner in LEED. I have a question regarding to EAp2. I am recently preparing LEED certificate report for a factory. However, I get a problem in achieving Minimum Energy Performance prerequisite (EAp2). More precisely, the objective of this prerequisite is to reduce building energy consumption by 18% in comparison to a baseline model. However, our proposed model only shows 12% energy reduction which is not enough to meet this prerequisite. The main reason is that the process loads are too high, which account for more than 70% total energy consumption. According to LEED Interpretation ID# 10291, for buildings where unregulated (process) loads account for more than 60% of project energy cost, the following alternative compliance path may be followed: 1. Create an energy model that includes only regulated loads and demonstrate that the project meets the minimum performance required for EAp2 by 18% energy consumption reduction. 2. Demonstrate that the proposed unregulated loads are 5% more efficient than the industry standard baseline or company average production efficiency by using the one of the three ECM approaches. → However, the explanation of document ECMs is not clear for me. Would you please give me explanation in more details how to calculate ECMs? Or what action should we take to meet this Energy & Atmosphere prerequisite for factory with such a high unregulated energy loads? In additionally, this factory will run a partial capacity of their machines. I means, for the 1st phase of operation, just some machines will be run, instead of all machines. In this case, can we get LEED certificated by calculating a part of process loads?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 04/05/2017 - 21:08

So you need to reduce the process energy use by 5% or more. The specific ECMs will depend on your specific process so it is hard to say what they might be. It could be something simple like premium efficiency motors, or a more efficient boiler or chiller. In those cases you can use 90.1 as your baseline. Something more specific will require you to establish an acceptable baseline for comparison to how the process is designed. The baseline should be standard industry practice in your area for a new factory of this type. If you are doing anything beyond that standard practice it may be eligible to could toward this savings. You must model the entire process load assuming it is running at full operation.

Fri, 04/07/2017 - 04:22

Thank you for your kind support, Marcus. In case I can prove a 5% process energy use, I will pass the minimum energy performance prerequisite. and will I achieve 4 points for Optimize energy performance credit?

Fri, 04/07/2017 - 13:29

Yes assuming you also meet the 18% minimum savings.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.