We refer to ASHRAE 90.1 Supplementary Addendum i which discuss the LPD of tradable surface on table 9.4.5. In this table, they allow the base site light power in "watts" to be added for the given zones such as zone 2 of 600 watt. Since the allowed LPD of all areas of this addendum is very low. Can we add the 600 watt as the power of the baseline?
Do we even have to follow the addendum? Can we just follow the standard?
Thanks
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
May 23, 2013 - 8:59 am
You do not have to follow the addendum, they are all optional. Looks like the base site lighting power replaced the additional 5% allowance, so yes you can add it.