FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Exterioir Lighting - Non tradable

Greetings, In the project I'm modeling, in the Proposed project there is a Building facades exterior lighting which LPD is bigger than the allowed values of 0.2 W/ft2. This lighting however is a special illumination which is controlled by separate control device independent of the other lighting systems. The question is: How to enter it in the Table 1.4.3B. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 12/01/2014 - 15:03

Non-tradable is modeled identically. If the proposed is greater than the Baseline allowance then model the same value as in the proposed in the baseline. Make sure your total exterior lighting is less than the overall baseline allowance (tradable + non-tradable) since exterior lighting is a mandatory provision.

Mon, 12/01/2014 - 15:13

Thanks for the reply. I've checked the total value and no matter that the Proposed facade is bigger then allowed, the total is less then the Baseline totals. At such situation which value to enter in the simulation - the project one or the max allowed. Thanks.

Mon, 12/01/2014 - 16:11

For the non-tradable the value should be identical based on the proposed value. For the tradable model the proposed as designed and the baseline per the ASHRAE allowance.

Tue, 12/02/2014 - 06:38

Thanks for the reply. Final question to this issue: If finally lighting facade of the Proposed makes the total exterior lighting bigger than BAseline, but in the same time the Proposed facades lighting is with characteristic corresponding to the exceptions specified in 9.4.5 b, how to enter the data in the table 1.4.3.B and refer to the mentioned exception . Thanks

Tue, 12/02/2014 - 14:29

In general facade lighting would not qualify under 9.4.5b unless it is illuminating a sign. If some of the exterior lighting qualifies under a 9.4.5 exception then it gets modeled identically in both models. Information on the exempted lighting would get entered in the Additional Notes box below the exterior lighting tables in Section 1.4.3B. Fully explain the purpose and area coverage as well as the wattage. If this covers a large area you should consider providing a separate document to explain how it qualifies for the exception.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.