NC-v4 WEc3:Cooling tower water use

Existing Campus CEP Cooling Towers

Hi all, 

I'm wondering if anyone has documented this credit for an existing campus CEP. The current cycles need to increased to achieve the minimum cycles of concentration. It is expected that the client will be happy to increase the cooling tower cycles, as they have previously noted that the cooling towers are using more water than they would like.

However, does anyone know what sort of documentation will be needed to demostrate this? Would a letter signed by the client that they will increase the cooling tower cycles be sufficient, or would another cooling tower water test be required to demostrate that they are achieving the maximum number of cycles (7.2 cycles; current cooling tower water test calculates the cycles to be 5.7).

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 05/13/2021 - 19:17

Hi Gregory, did you figure out this answer? We are coming up on a similar campus-project question. Thanks, Annie