FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Existing Building Fenestration

According to ASHRAE 90.1-2007 Table G3.1.5 (f) for existing building envelopes, the baseline building design shall reflect existing conditions prior to any revisions that are part of the scope of work being evaluated. Does this mean that for an existing fully glazed building (80% of gross above-grade wall area) the baseline building will meet the same portion of fenestration (80%)?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/11/2014 - 17:24

If the existing building is 80% then the baseline would be 80% assuming the renovation remained at 80%. If the glazing area was reduced during the renovation then the baseline glazing area would also be reduced.

Thu, 12/11/2014 - 17:52

Thank you Marcus!

Thu, 11/26/2015 - 16:09

When it comes to complete Table 1.4.2A (Shading&Orientation) of the Excel Spreadsheet a message appears stating that Baseline vertical glazing areas limited to 40% of gross above-grade wall area per Table G3.1#5(c). However, our project is 100% major renovation with no additions and a glazing area of 72% which remains the same after the renovation. We can still have a baseline with 72% glazing in that case (according to G3.1#5(f)), cant' we?

Mon, 11/30/2015 - 16:38

In my opinion yes you can. G3.1#5f would over-rule G3.1#5c for an existing building. The Table 1.4.2A note is just related to G3.1#5c.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.