(Appologies for double posting, I posted the same question on the v4-forum. Just realized it is probably more appropriate on the v4.1 page.)
Hi everyone
We are trying to make some strategic decisions and would be happy about some feedback. First a short summary, two questions are below.
Situation is an existing office building with moderate renovations (C+S), some key points:
- nearly everywhere curtainwall facade, U-value facade around 2.4 W/(m²K) -> the facade is in good condition and will not be renovated, apart from some solar shading that must be redone
- roofs will be renovated and insulated
- cooling was provided through air with inefficient chillers -> after renovation, there will be cooled ceilings and purchased chilled water, air volume based on hygienic requirements
- heating is and remains purchased heat with radiators and floor heating
- lighting is replaced everywhere by LED
Using v4:
- The building envelope of the baseline building would be the same as the existing building, prior to renovations. As the envelope barely changes, this will provided hardly any energy savings.
- DES:
- Path 1: both baseline and proposed modelled with purchased heat and chilled water, only downstream equipment, identical utility rates, efficiency 100 % -> no energy savings
- Path 2: Baseline per Appendix G (efficiency 80%), DES virtual plant (efficiency maybe 85 %)
- Evaluation: comparison of energy costs -> depending on DES modelling path, but we don't expect high energy cost savings.
Using v4.1:
- The building envelope of the baseline building would be based on App. G in ASHRAE 90.1-2016 (Table G3.4-4), which would result in moderate savings in heating and cooling energy.
- DES:
- Evaluation:
Question 1: Would you recommend v4 or v4.1 for this project? It is rather limited information, feel free to ask follow-up questions.
Question 2: Is it correct, regarding DES modelling, that path 1 does not allow to take credit for GHG savings?
Thank you for your time!
Sarah