FAQs about EAp2 :

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Existing and New Construction

We have a building that contains both existing and new construction. I wonder how we should determine the LEED points we will achieve given certain percentage savings. Is it based on 60% rule? Thanks in advance

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 07/31/2015 - 13:24

The % savings is calculated based on a weighted average of new to existing area for the project. So for example if the area is 50% new and 50% existing you would split the difference between the 10% (new) and 5% (existing) and would need 7.5% to meet the prerequisite requirements.

Fri, 07/31/2015 - 14:04

Thanks Marcus. How we should document this on LEED online? It doesnt give us an option to input the savings for new and existing separately. Instead, it automatically calculate the savings and points achieved. Also, the building has three part: new, renovated existing and unrenovated portion.

Fri, 07/31/2015 - 14:00

The prerequisite form will accurately calculate the percentage and points based on the ratio of new to existing area. This information gets entered in one of the project information forms and automatically transfers to the EAp2 form within LEED Online.

Fri, 07/31/2015 - 14:13

Let me elaborate my question: I can enter the % of new and existing floor area but cant enter the savings % for them. Also, I modeled all those spaces in the same model so I don't know if it is possible to separate the savings for each portion. Especially the cooling, heating and fan energy cannot be separated easily since they have non-linear curve. And another thing is that, once we have the savings, say 15% prorated, how many points should we get? Are we using New buildings or existing threshold? I wonder if the reviewer can accept if the building has more than 60% existing area, we can use the existing building threshold

Fri, 07/31/2015 - 15:23

You don't enter the % savings. The form calculates it. You don't separate the savings for each portion. The weighted average is applied to the total. You are using a blend of new and existing to determine the thresholds for the points. In my previous example (50% new, 50% existing) the prerequisite starts at 7.5%, 1 point would be 10%, 2 points would be 12%, 6 points would be 20%, etc. Basically you are creating your own set of thresholds for the points based on the ratio of new to existing in your project. No a 60% existing area cannot use the existing thresholds. It just does not work that way.

Fri, 07/31/2015 - 15:55

Thanks for the clarification Marcus. It is clear to me now.