Forum discussion

NC-2009 IEQp1:Minimum indoor air quality performance

Exhaust Requeriments with Natural Ventilation

hi all, Can you meet the prerequisite using paragraph 5.1 (Natural ventilation) from Standard 62.1-2007 for areas that require exhaust system (i.e. toilets, kitchens, etc.)? Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 07/29/2013 - 22:14

Hi- I don't see why not. The prerequisite does not address the required exhaust, but just the required outdoor air supply (whether natural or mechanical).

Mon, 07/29/2013 - 22:28

I've contacted both gbci and ASHRAE on this and they both confirmed that section 5.1 does not substitute exhaust requirements. Section 5.1 substitutes OA supply only.

Tue, 07/30/2013 - 14:47

You may find Andrew Mitchell, P.E.'s response from a question about kitchen exhaust below helpful: "per LEED CIR 10248, any mechanically ventilated kitchen must meet the exhaust requirements of ASHRAE 62.1 Table 6-4 (exhausted to the outside). Naturally ventilated kitchens do not require exhaust tot he outdoors. Please see the ruling language here: http://www.usgbc.org/leed-interpretations?keys=10248"

Tue, 07/30/2013 - 15:00

Also, I suppose I should qualify my statement above that "the prerequisite does not address the required exhaust". Actually, while the LEED credit form does not require specific exhaust data or calculations, mechanically ventilated spaces do have to comply with ASHRAE 62.1-2007 section 6, which includes required exhaust.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.