We have 4 person meeting rooms that are typically used for less than an hour at a time, yet during our GBCI audit a comment was made that these spaces need to be controlled individually. We were asked to:
"Provide a narrative and supporting documentation such as drawings, control diagrams, and cut sheets to demonstrate that each individual private office and specialty occupancies have active controls; and controls are capable of sensing space use and modulating the HVAC system in response to space demand."
Would adding an exhaust fan with a thermostat to each of these rooms be an acceptable solution to meet the intent of the credit? The rooms could have returns ducted to the adjacent open office area. We are hoping that this could be a more cost effective solution than installing a VAV at each location. Could it be an on/off switch and operate like the IEQ 6.1wher a user can control the funtion instead of a sensor?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
monu goyal
Environmental EngineerMetadesign Architects Pvt. Ltd.
51 thumbs up
April 9, 2012 - 3:37 am
we have also received same comment from GBCI for our final review to provide active control for some of private office. We also need help how can we complete this requirement without ant cost escalation.
Erik Dyrr
Director, Sustainable Buildings and OperationsKEMA
80 thumbs up
April 9, 2012 - 2:05 pm
Rob and Monu,
I don't think the exhaust fan approach will meet the intent of the credit. The intent is energy savings by reducing airflow, and fan power, for unoccupied areas. The requirement in the reference guide is..."The system must be capable of modulating air-handling units (AHUs) and zone minimum supply volume below 0.30 cubic feet per minute per square foot of supply volume for standard variable air volume (VAV) terminals, or below 22.5% of the peak design flow rate for fan-powered VAV boxes. For spaces where the minimum outdoor air flow exceeds the minimum supply volumes specified here, use occupant sensors or demand-controlled ventilation to achieve these minimum supply volumes."
I don't know a cost effective way for meeting this credit with a standard VAV system. If anyone does please share.