Dear All,

We're working on the certification of a restaurant where the kitchen has an outdoor air (OA) rate of 2350 CFM, supply air at 8000 CFM, and an exhaust rate of 3675 CFM. eQUEST treats the difference between exhaust air and outside air as additional outdoor air requirement. The input summary (SV-A reports) shows that both the zone and as a result, the building are taking in roughly 1325 CFM extra outside air. Is there a workaround to this?

The design intent, I'm told, was to pull in the make up air for the difference from the four adjacent HVAC zones and not necessarily through the same zone as outdoor air.

Thank you,
Ramana.