FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

EV chargers

We are building a parking structure to support the LEED project building and providing EV chargers. Must the EV chargers be included in our LEED energy model? We are providing PV panels to provide renewable energy for both building energy use and the EV chargers.

 

Thanks in advance.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 03/05/2018 - 17:45

Yes. All energy use in and associated with the project must be included.

Thu, 05/17/2018 - 22:31

Follow up question - do we include all EV chargers being occupied 100% of business hours, or can we take a 75% utilization rate if we expect that not all will be occupied? Should we assume 8 hour charge per day?   Thanks

Thu, 05/17/2018 - 22:40

You could apply a diversity. Regarding the number of charge hours/day - that would depend on the charger. Some would draw a charge all day, some would be charged in less than that. Also depends on the level of charge the vehicle has when it starts charging. I would suggest that you seek to find some studies on EV charger operation so you could make some more informed assumptions. Sounds like you have a bit of a research project. Let us know what you find.

Fri, 05/18/2018 - 01:12

Marcus, what do you mean by applying a diversity?  Thanks, I think we are using the 4-hour chargers so we would assume they are used twice per day at 4 hours each per charge.

Fri, 05/18/2018 - 13:07

A diversity is the fraction of the total within each hour in an energy modeling schedule. Your 75% is a diversity.

Mon, 12/19/2022 - 17:47

https://www.usgbc.org/leedaddenda/10499 Based on this LEED interpration, I would say that you can exclude them.  