FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Equipment efficiencies / DX Cooling Coil EER and COP

Hi all.

Question about ASHRAE 90.1 Baseline equipment efficiencies.Project is using System 5 with a Load of around 400kBtu/h.  Table 6.8.1A shows the minimum efficiency to be 9.8

 

Now to my question:

In my baseline (energyplus /openstudio) model. I have been entering my EER (9.8) as COP(2.872) under an input in the DX Coil named "Rated High Speed COP". But when I look at the energy plus equipment summary output tables for DX cooling coils I see a rated standard COP(w/w)  output of 2.55 and a EER (Btu/W-H) of 8.71. To try and find a solution I went into the eneryplus reference material and saw that it said that the COP input is "Gross cooling capacity divided by power input to the compressor and out door fan, but DOES NOT include supply fan heat or supply fan electrical energy input." So I was not sure if if those lower COP and lower EER values in the output table would be considered (by LEED Reviewer) correct or if I should try and add the missing supply fan heat and electrical energy input so that I can  increase my EER and COP values to match 90.1. Then I thought I should take another look at ASHRAE G3.1.2.1 Equipment efficiencies and saw it said " all HVAC equipment in the baseline building design shall be modeled at the minimum efficiency levels, both part load and full load, in accordance with section 6.4. Where efficiencies ratings, such as EER and COP, include fan energy, the descriptor shall be broken down into its components so that the fan energy can be modeled separately". So it sounds like I am not suppose to include my supply fan energy in my coil EER. So does that mean I need to remove the supply fan power from my 9.8 EER so that it matches the energyplus input description?

 

Thanks in advance,

FP

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Sun, 11/05/2017 - 22:03

I believe i found my answer in this document on page 37 and 38  

Mon, 11/06/2017 - 06:59

The real answer is pretty complex. I suggest you ask on the energyplus forum and read posts Jim Dirks. Essentially, you are entering rating condition operating point values that act together with the normalized performance curves of the dx machine only. The ARI ratings are for the entire machine meaning dx coil + fan + other. So for the proposed case that's no problem, you model the machine as it is, but the baseline is fictitious. Really, you need to adjust the curves so that the ARI rating results in the e+ results summary table are as those in the standard. There is no published way on how to adjust the curves to do this, as many different curves could lead to the same ARI rating values. Jim has suggested a defensible method. The other method is to model a real machine for the baseline with the required rated capacity and make sure the ARI rating values are "better" than the baseline, i.e. error on the conservitive side.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.