You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium forForum discussion
NC-2009 EAp2: Minimum Energy Performance
LEEDuser is supported by our premium members, not by advertisers.
Go premium forTo post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.
A portion of our building envelope is historic. Can we exclude it from our model?
For an existing building, do I need to rotate the model?
Our process load is higher than 25%. Do we have to justify that?
Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?
Can mezzanines open to floors below be excluded from the energy model?
How do I provide a zip code for an international location?
For a project outside the U.S., how do I determine the climate zone?
For a project outside the U.S., how do I determine the Target Finder score?
Do hotel rooms need automatic light shut-off control?
How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?
The Section 9 space-by-space method does not include residential space types. What should I use?
Can the Passive House Planning Package (PHPP) be used to energy model for LEED?
Which baseline HVAC system do I use if my building has no heating or air conditioning?
Our project has a diesel backup generator. Should we include it in our energy model?
Can SHGC be higher in the proposed than in the baseline model?
Jean Marais
b.i.g. Bechtold DesignBuilder Expert832 thumbs up
November 9, 2012 - 2:06 am
Very good question. Ideally all the systems, but if I were a reviewer, I would only look at the fan(s), chiller and boiler sizing. Here the sizing has the greatest impact on efficiency. If your coil is oversized, it may only impact on the pumping power. Pumping power inturn is very roughly estimated as no pressure drop in the piping is required to be dynamically simulated in the simulation. For the baseline pumping power is a function of mass flow. Electrical equipment is also not that critical in my opinion. Most softwares are limited in what they can actually size, by internal model assumptions.
Anyone else?
PAWAN DAHIWAL
10 thumbs up
November 9, 2012 - 3:22 am
thanks sir. your comment really help me. I little bit wondered when i listen from my colleague that, oversizing can be done at system level or zone level but not at both. according to me, system level is what we can say it a source which generate a medium for HVAC it may be include but not limited to boilers, chillers etc but i am not confirmed about zone level, it might include fans or else. So, according to you can we oversize these all parts by 25 and 15 %?? Any thoughts??????
+++++ can you please give me more info on zone level equipments oversizing?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
November 9, 2012 - 10:22 am
Correct it can't be done at both the system and zone level. In general it is done at the zone or the plant level, usually the zone level. Again it can't be at both.