Are the requirements in LEED Healthcare v4 - EQc6 - Interior Lighting limited to the following attached herein or are the ones mentioned in this websites Viewpoint section?:
(portion of credit's text in Reference Guide)
HEALTHCARE
Provide individual lighting controls for at least 90% of individual occupant spaces in staff areas.
For at least 90% of patient positions, provide lighting controls that are readily accessible from the patient’s bed.
In multioccupant patient spaces, the controls must be individual lighting controls. In private rooms, also provide
exterior window shades, blinds, or curtain controls that are readily accessible from the patient’s bed. Exceptions
include in-patient critical care, pediatric, and psychiatric patient rooms.
For all shared multioccupant spaces, provide multizone control systems that enable occupants to adjust the
lighting to meet group needs and preferences, with at least three lighting levels or scenes (on, off, midlevel).
Midlevel is 30% to 70% of the maximum illumination level (not including daylight contributions).