NC-2009 IEQp1:Minimum indoor air quality performance

Engineered ventilation system - operable windows

In our high-rise multifamily building project, we are trying to demonstrate IEQp1 compliance for living rooms & bedrooms by showing an engineered ventilation system whereby toilet exhaust fans draw enough outside air through operable windows in said rooms to satisfy 62.1 rates. However, the LEED reviewer is asking for documentation on how the required ventilation rates would be met when the windows are shut closed. From my understanding, simply having operable windows is sufficient to demonstrate 62.1 compliance, and since the windows can be opened or closed by the occupants when needed, it is not necessary to show compliance with windows closed. Can anyone add their thoughts on this? Thanks!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 09/02/2014 - 22:31

There are two paths for showing ventilation compliance for an individual space or ventilation zone: Path 1 - Mechanical ventilation. In this case, you cannot take credit for opening windows. And this is where ASHRAE 62.1 mechanical ventilation rates apply. Path 2 - Natural ventilation. In this case for NC2009, operable windows are sufficient, subject to area and distance requirements for the windows. You could probably make a special circumstances or alternative compliance case for extending the distance from the window due to the assistance of the toilet exhaust fan, but ASHRAE 62.1 ventilation rate do not really apply to the natural ventilation case. I think you will get more traction by clearly identifying which path you are taking (either Mechanical Ventilation or Natural Ventilation) and sticking to that path. If you blend the criteria for the two paths together indiscriminately, it will be unlikely to be accepted. For example, you could say for Alternative Compliance that you are using the natural ventilation path, show that you have the required percentage of operable window area, and then introduce the concept of "fan-assisted" natural ventilation to justify any areas farther than the 25 feet criteria away from the window.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.