FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

EnergyPro DOE-2 Output Report: system and plant throttling range %

Hi all,

We are using EnergyPro v6 for our LEED modeling. Per the Advanced Energy Modeling for LEED Technical Manual v2.0 p.16, the DOE2 reports show the unmet load hours as a throttling range that needs to be under 3.4%. The % is the equivalent of <300h for compliance with the ASHRAE and LEED requirements. The guide does not clarify if the requirement applies to both system and plant throttling range. Per the word selection it seems that it focuses on the system %.

My question is whether for the LEED submission using a DOE2 report, both system and plant need to be under 3.4% as a throttling range?

Reason being that in LEED submissions with other software, the unmet load hours are approached differently showing an overall discrepancy between baseline and proposed for heating and cooling, and are not broken down at both a system and plant level.

Please advise.

Regards,

Maria

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 10/26/2017 - 19:20

The overall system should not exceed 300 hours including both the plant and the system levels. Sometimes with DOE2 software you need to dig a bit deeper than the BEPS/BEPU reporting. Many of those system and plants hours could be coincident and therefore are double counted. I can't remember the name of the DOE2 report you will need to find but I do recall seeing one that was used when the throttling range percentage was too high. If you can't find it ask again and I will dig it out.