FAQs about EAp2 :

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Energy source for Reheat

Hello, For the baseline building, does the REHEAT energy source for a VAV system need to be identical to the proposed reheat source, or is it as per the main heating source? For example, my proposed system is a VAV with diesel boilers for space heating. The VAV is also equipped with Electrical Reheat boxes in each zone. For my baseline, System #7 applies. The baseline heating system is therefore a fuel boiler, but what about the baseline reheat? Does it have to be similar to the baseline principal space heating source (i.e., Hot Water Reheat), or can it be similar to the proposed reheat source (i.e., Electrical Reheat)? Thanks!

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 01/22/2014 - 16:29

You have a hybrid system so it comes under the fossil fuel column. The reheat in a system 7 must come from the boiler system. There is no electric heat in this baseline.

Thu, 01/30/2014 - 10:31

Thanks Marcus.