Hi, I am working on a office building of about 15,000sqm using AHU with underfloor system. The following are the HVAC baseline that I have input into the HAP software:

Chiller:
2 screw chiller sized equally
Chilled Water Supply = 6.7 deg C
Chilled Water Return = 13 deg C

Pumps:
Primary pumps only
CHW Pump Power = 349 kW / 1000L/s
CW Pump Power = 310 kW / 1000L/s

Heat Rejection - Cooling Tower:
Condenser Water Supply = 29 deg C
Condenser Water Return = 34.6 deg C

Variable Speed AHU with underfloor outlet (System 8):
Air flowrate = autosized with 1.15x for cooling
Power = 0.0021 kW per L/s
VAV Box opening = 50% minimum

// Are the above input correct?

Also, I was browsing through Appendix G and under G3.1.3.14, it states that the "Fans in parallel VAV fan-powered boxes ... shall be modeled with 0.74 W per L/s fan power", which is different from Table G3.1.2.9.

Can I understand when shall 0.74 W per L/s be used and when shall Table G3.1.2.9 be used?