I’m modelling a System 8 baseline model according to ASHRAE 90.1-2010.
An exhaust energy recovery system is needed according to table 6.5.6.1.
Since the building is located in climate zone 4A (Milan, Italy) no economizer is requested.
Shall the heat exchanger have no control logics? No bypass?
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5859 thumbs up
June 20, 2018 - 10:21 am
That's correct there are no controls or bypass.