Forum discussion

NC-2009 EAc1:Optimize energy performance

Energy Performance : Automated Lightning and HVAC system

We Desined a Dormitory Building ( NC ) already constructed and in operation. Each door of the bedrooms has a card reader connected to a BMS ( Building Management System ). When the card is inserted the signal is sent to receivers that allow full user operation of lightning and confort levels. Once the tenant remove the card from the reader task, confort systems turn to energy saving/stand-by mode. We finally dind't find any method on ASHRAE standards to submit this kind of energy consumption, and we can't achieve the LEED EA credits due to the impossible calculation of the real energy use of the building. We just found a similar method to calculate energy saving only fot lightning system, but not for HVAC system; this issue let our building not pursuiting the necessary treshold for achieving the LEED Certification. I Hope someone that often use LEED rating systems can help us. Kindly Regards. Marco Valerio Ceccotti

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 12/15/2015 - 19:02

You can claim these savings. It will likely require schedule changes and therefore an exceptional calculation. See Appendix D4 in the Advanced Energy Modeling guide for LEED Technical Manual for one idea. You should also research other methodologies for claiming the savings from this kind of controls. You will likely have to propose a methodology to claim the savings. You can try this in the review process or seek feedback from USGBC ahead of time through an interpretation.

Fri, 12/18/2015 - 18:14

Marcus, thanks for your quick and usefull answer. I'd like, in the next days, to have a comment from you about our incoming work. Regards

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.