We are working on an elementary school project and we're trying to correctly model the sun shading. We understand we should "count" the benefits from permanent sun shading devices designed at windows (for example, projections from the building). We also understand that you cannot "count" any shading benefits from adjacent buildings on neighboring sites (because perhaps that other building will be torn down in the future).
However, we believe we should model the shading effects on our own building. In other words, one wing of the school is 2 stories and the other wing of the building is one story. The two story wing will shade the single story wing for at least part of the day. Is this considered adjacent building shading? Or, can we submit it as "self shading".
We are modeling the project using Trane Trace which calls building shading "adjacent building shading"- which is not to be counted by LEED. We've categorized it as adjacent building shading simply because Trane Trace doesn't have a "self shading" option.
Is self shading a legitimate strategy to demonstrate projected energy savings? And, if so, how can we communicate to our reviewer that we really mean "self shading" and not "adjacent building shading".
And no, there is no way the 2 story wing of the building will ever be demolished.
Any help is appreciated.
Joanna
Christopher Schaffner
CEO & FounderThe Green Engineer
LEEDuser Expert
963 thumbs up
May 28, 2010 - 10:44 am
Self shading is definitely a legitimate strategy. Some software packages can pick this up "automatically". I don't believe Trace has that capability.
I would do just what you described above, and include an explanatory narrative in your LEED submission.
Peter Doo
PresidentDoo Consulting LLC
203 thumbs up
April 2, 2014 - 5:09 pm
On Demand Water Heaters
Any advice on how to capture savings from these devices in energy modeling? Our engineer is struggling.
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5928 thumbs up
April 3, 2014 - 10:23 am
Hi Peter,
The baseline is required to use the same type of equipment so the only savings you can capture related to this equipment is the difference in efficiency between the proposed water heater and the baseline defined in ASHRAE 90.1-2007 Table 7.8.