Greetings. I am working on a Commercial interior project pursuing the EAP2, and I chose the section 11 as an alternative to prescriptive approach, but, i am a little bit confused about how to simulate the envelope (u factor, shading coefficient..) in Energy Cost Budget (ECB) and Design Energy Cost (DEC). In table 11.3.1#5 say that the ECB shall be modeled with the U factor from section 5.5 and SHGC shall be the maximum allowed for the climate and orientation. In the Credit 1.3, table 2#5 it says that existing building envelope must be used. Then I do not know how to simulate it in the ECB, besides a film will be added to the window glass in the commercial interior space in order to reduce the vertical fenestration shading coefficient. Thanks for your advice

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Tue, 08/14/2012 - 15:59

For a CI project it makes sense to model the existing building envelope in both models since it is existing and the exception in 11.3.1#5 applies. If the window film is in the scope of work then model the existing windows in the Baseline and the same windows with the film in the Proposed.

Wed, 09/05/2012 - 22:42

Thanks Marcus. just an additional question. adding a film to the windows could be consider as an addition and apply to the exception in 11.3.1#5? since the only change in the existing fenestration is the film. just to make sure, in order to model the same envelope in the ECB and DEC in a commercial interior, the scope of the project must not included changes in the existing façade? Thanks in advance.

Thu, 09/06/2012 - 13:23

The addition they are referring to is a building addition not adding a film to an existing building. See 4.2.1.2 referenced in the exception to 11.3.1#5.

Fri, 10/19/2012 - 19:14

Thanks a lot Marcus is very usefull your answer. I have a last question, I'm using the simulation method to met the prerequisite, but when I enter to the form of EAP2 in leedonline I don't see where introduce the simulation outputs. Could you tell me what Should I fill if I am working with simulation path? Thanks again for your advice.

Fri, 10/19/2012 - 19:48

I don't see it either. So check the special circumstances box at the bottom of the form. Write a brief narrative in the box that appears. Then upload your modeling results. Provide information similar to what you would provide for a BD+C Appendix G submission.