The design team is specifying an electric instantaneous water heater on a project we are working with. The project is located in Argentina.
Since this type of water heater is not listed in table 7.8, of 90.1-2007, do we have to comply with any minimum performance requirements?
In the baseline simulation, should we use an electric water heater (with storage tank) sized according to load calculations?
Any hints are welcomed.
Regards,
Anderson
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
June 4, 2014 - 9:35 am
There is nothing to comply with so there is no minimum.
Yes the baseline is electric resistance - see Table G3.1-11 Baseline (b).