We have an MEP engineer that is calculating peak loads at about 6 times passive house levels on a large commercial building that is at or near passive house levels of insulation and air infiltration. We suspect one reason is that he is figuring a 50% efficiency level for the ERV. We are showing him ERV systems with 80-90% efficiency, but they are telling us that the actual efficiency is never that high in practice because of failure to adequately maintain and run the systems at peak efficiency.
Any guidance on a reasonable ERV efficiency for peak load calculations and/or other things we might ask about so that we don't over or undersize peak loads?
90.1-16 requires energy recover systems (prescriptive) to perform at an enthalpy recover ratio of at least 50% (change in the enthalpy of outdoor air divided by the difference between the outdoor air and entering exhaust air enthalpy, expressed as a %, calculated using units of Btu/lb-dry air). So I would assume that as an absolute worst case scenerio. Double check that airflows are balanced and that you all are thinking / looking / talking about / entering is in terms of total energy / enthalpy and not just sensible energy?