The efficiency of the boiler that I’m modeling has to respect Table 6.8.1F of ASHRAE 90.1:2007. More precisely, the thermal efficiency Et shall be equal to 80% according to the test procedure 10 CGR Part 431.
The boiler of the baseline model doesn't correspond to a real boiler, but to a reference boiler, therefore I’m wondering whether modeling the thermal efficiency of the baseline model as constant would be acceptable. If I have to use an efficiency curve, how should that curve be? I mean, should the thermal efficiency increase with the boiler part-load ratio? Should the curve be function of the water temperature?
With Regards
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Marcus Sheffer
LEED Fellow7group / Energy Opportunities
LEEDuser Expert
5909 thumbs up
August 13, 2012 - 10:50 am
No boiler efficiency curve is required for the baseline.