CI-2009 EAp2:Minimum energy performance

EER to COP conversion

Hi, I am trying to document the efficiency for comms room AC units and a data centre down flow AC units. As we are in Europe the efficiency is quoted by manufacturers in EER. ASHRAE 90.1 2007 Table 6.8.1D refers to COP. Does anyone have an accepted conversion. e.g an EER will have a COP of ???

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 01/07/2016 - 14:32

COP = (EER)/3.413

Thu, 01/07/2016 - 14:45

Thanks. Is there any exemptions for smaller AC units. I have some AC units that have an EER of 3.57 and this would equate to a COP of 1.046 which is less than the minimum performance for LEED (2.49). I can't get units with a COP of 2.49 as this would mean an EER of 8.5 which is not available in the marketplace ? Is my interpretation wrong ?

Fri, 01/08/2016 - 20:32

I am not aware of any exceptions for small air conditioners. The EER of the units you mention is well below what is legal in the US. These minimum efficiencies are mandatory for LEED projects.