EAc1.3 Option 2: Baseline vs Alternate Baseline

I am working on a small building that is pursuing LEED CI. The building is comprised of two tenant spaces, office and restaurant/dining. The office space (pursuing LEED CI) is completely finished and occupied while the restaurant/dining is unfinished shell space. The restaurant/dining area does include Base Building HVAC equipment, plumbing and lighting for permit. I would like to model the building using the Option 2 Baseline method. However, since the restaurant/dining is unfinished I am unsure how to model this space for lighting. Can I assume ASHRAE 90.1 values per Section 11 or should I use the Base Building lighting power densities which only include emergency lighting? Your feedback is welcome.

2

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 09/10/2014 - 12:31

You model it the same as the Baseline allowance.

Wed, 09/10/2014 - 13:07

Marcus, thank you for your response. Now that I read my question, I'm not sure I was clear in which space I had the question. It is the restaurant/dining space that I was unsure of. If I use Base Building (Core and Shell) lighting it will only include emergency lighting as the space is not built out. The other option, which I used in the LEED submission is to use the "not to exceed" LPD value listed in the Tenant Lease Agreement. Thanks again.

Wed, 09/10/2014 - 13:26

Perhaps it was my answer which was not clear. Baseline means according to Appendix G/Section 11. If you have a lighting design or a not to exceed LPD in the lease agreement then you can use those values to claim savings. However, for this credit under Option 2 I think you are supposed to hold all of the non-HVAC modeling inputs neutral (i.e. the same) to determine the HVAC percentage only. The procedure is in the Reference Guide.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.