The problem I am having is that I have to select a system for the baseline model which is System 7 VAV with Reheat, based on the advise of ASHRAE Table G3.1.1A , however the proposed system for the  building is to be a FCU system with a chiller, gas fired boiler and AHU supplying tempered air.  I thought the systems had to be similar in some way.
Or do I just have to have the same amount of AHU's for example?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 12/21/2017 - 16:14

Sometimes the baseline system is very different than the proposed system. Make sure to follow the full guidance for the baseline system in G3.1.1. For example with a system #7 there needs to be a system per floor so it may not have the same amount of AHUs as the proposed.