Forum discussion

CI-2009 EAp2:Minimum energy performance

EA Pr 2 - Water Heating Equipment

I have a 12kW electric water cylinder and a 12kW direct gas fired water heater. Can anyone please explain what I need to check to ensure the performance requirements comply with ASHRAE 90.1 2007 table 7.8. I dont understand the rating condition and performance required headings.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 01/06/2016 - 15:19

The Subcategory or Rating Condition refers to the type of water heater and/or its storage capacity. The Performance Required is a formula used to determine the minimum efficiency of the equipment. So for a 12 kW electric, tank-type water heater the formula you use is 0.93–0.00132V EF. The note below the table identifies the variables V and EF. A clearer way to see this formula would be EF = 0.93–0.00132V. So put the volume of the tank in the equation and calculate the EF.

Wed, 01/06/2016 - 15:44

Great thanks.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.