Duct adhesives

All HVAC ducts will have an adhesive, some sort of strip, that goes around the duct connections. Does anybody know what will the limit be for this adhesive? Thank you very much.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 06/20/2013 - 14:11

Please see memo below explaining that Duct sealants are in the catagory of “Other” in the SCAQMD VOC Limits table has a maximum limit of 420 g/l. Technical Resources Bulletin July 31, 2009 TRB #9-09 To: SMACNA Members From: Technical Resources Department Subject: UPDATE on HVAC Duct Sealant Usage Requirements on USGBC LEED® Projects The following bulletin is an update to TRB #4-09 issued March 27, 2009 with the Subject: HVAC Duct Sealant Usage Requirements on USGBC LEED® Projects. In response to the following Credit Interpretation Request (CIR): “How does a project team classify duct sealants for application under EQc4.1?” the USGBC issued the following ruling: “Project teams may classify duct sealants under “Other”, as listed in the SCAQMD VOC Limits table.” The category of “Other” in the SCAQMD VOC Limits table has a maximum limit of 420 g/l. This should allow most if not all duct sealants to be utilized on LEED® projects, and permit the proper sealing of ductwork at temperatures below 40°F (5°C). In keeping with SMACNA’s policy on sustainability, contractors are encouraged to use products with the least environmental impact for the intended application and jobsite conditions.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.