EBOM-2009 WEc4:Cooling tower water management

Drycoolers

We work on a project that has Drycoolers, all water user is non-potable. Since there is no closed loop and make up water this system there no treatment. Can we pursue both 4.1 and 4.2 credits?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 12/14/2012 - 17:58

Hi Wagner This is a good question. And I'm not sure if I have a 100% certain answer, but it seems to me that you would be eligible for WEc4.2 because the system in and of itself uses no potable water. As for WEc4.1, I'm inclined to say that your project would not be eligible - the intent of the credit is for water quality (not quantity as in WEc4.2), so you'd need to be using water to achieve it. You can always try and submit both as I'm assuming the documentation would be similar by submitting an Alternative Compliance Path option. But if you want a more definitive answer, I'd suggest submitting a CIR. Thanks

Mon, 09/28/2015 - 16:31

Hi Hanna, is it then reasonable to even consider it as an exemplary performance since using 100% non-potable water? Thanks

Wed, 05/17/2017 - 09:50

Hi Eleftherios, Could you share with us if you earned this exemplary performance point at this project? thank you!