NC-2009 IEQp1:Minimum IAQ Performance

Dorm Suite Ventilation

Our project is a large high rise dorm consisting of 4-person suites arranged typically as a 2BR and two 1BR's connected by a short inner hallway. The suite has a shared single bathroom accessible from the inner hallway. The inner hallway is very narrow and not occupiable for any duration. Our current scheme includes bathroom exhaust at 50-cfm continuous. Fresh air (neutral, i100% outside air) is delivered at 50-cfm to the hallway only (not each bedroom). The 50-cfm of OA meets the total suite ventilation requirement based on the 5-cfm/person + 0.06 cfm/sf requirement of ASHRAE 62.1-2007. The doors to each bedroom are undercut to allow the fresh air into the bedrooms. Would the above scheme meet the requirements for mechanical ventilation per ASHRAE 62.1 for all spaces in the dorm suite?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/06/2015 - 23:21

No, that would not meet the requirements for mechanical ventilation. Mechanical ventilation should have some way of making the air come into the occupiable space.

Sat, 11/07/2015 - 02:08

Any chance the bedrooms have operable windows such that they meet the naturally ventilation requirements in terms of size, while the inner hallway is mechanically ventilated?