FAQs about EAp2 :

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

Can I claim exterior lighting savings for canopy lighting even though a baseline model cannot include shading elements?

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

View answers »

Forum discussion

NC-2009 EAp2:Minimum Energy Performance

Does PPR piping need insulation?

We have run into a situation with piping material used in a hotwater distribution system. Our client is using Polypropelene piping. (PPR) The thermal transmitance of this piping is in the range of .1-.22 W/m.k. Do they need insulation for this piping? Thermal transmitance for copper and iron piping is 400 and 80 W/m.k.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Thu, 11/01/2012 - 19:01

Looks like it needs insulated unless one of the exceptions to 6.4.4.1.3 applies.

Thu, 11/01/2012 - 20:46

Rudolph, take a look at ASHRAE 90.1-2010, Table 6.8.3A, note 'e'. It addresses the topic of non-metallic pipe. As LEED 2009 allows you to use addenda to ASHRAE 90.1-2007, if you can find the addendum that added note 'e' and comply with that particular addendum in its entirety, you might be able to get by with using PP piping without insulation (or at least reduced insulation). Good luck!

Thu, 11/01/2012 - 21:48

Make sure since this is a mandatory provision. In my experience even plastic pipe will have enough heat loss that pipe insulation makes sense. Seek not the exception to enable lower levels of efficiency but seek to improve energy efficiency.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.