Hello everyone, I am working on the documentation of a Multi zone project for the cooling conditions in this case should the "Zone Primary Air flow Vpz" be equal to the "Zone Discharge Airflow Vdz"?

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 04/28/2017 - 14:49

The primary flow is what comes from the AHU (mixed return and OA). The discharge airflow is the primary flow plus any local recirculation. If there is no recirculation, then they will be the same number.