NC-2009 MRc4:Recycled content

Do I include plumbing fixtures in the materials scope

Hi I know accessories are included but are actual plumbing fixtures included in these calcs? They are not with Divs 3-10

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 01/23/2015 - 22:00

Erika - You answered your own question - since plumbing fixtures are not specified in the Divisions outlined for the MR credits (Divisions 03-10 and the required sections in 31 and 32), they are NOT included in the calculations. In addition, the credit requirements specifically say: "Mechanical, electrical and plumbing components, and specialty items such as elevators and equipment cannot be included in all calculations."

Fri, 01/23/2015 - 21:56

Thank ya, thank ya