CS-v4 EAc2:Optimize energy performance

District Cooling Confirmation for Path 1 & Path 2

Hi,

We seek your confirmation on the correct energy modeling approach for a project served by a District Cooling Plant (DCP) with a coefficient of performance (COP) of 6.2, in accordance with ASHRAE 90.1-2010 and LEED requirements.

The baseline HVAC systems for the project  have been selected as System 06 – Packaged VAV with Reheat, based on conditioned floor area, per Appendix G.

We request confirmation on the following two modeling approaches:

  1. DES Path 1 – ASHRAE 90.1-2010, Option 1 (Simplified DES Approach):
    • Under this approach, the baseline building systems are converted from System 06 to System 08 (VAV with Chilled Water Plant).
    • The baseline chilled water plant efficiency is modeled using the same district cooling plant efficiency as the proposed case (COP = 6.2).
    • The proposed case has been utilized using the actual district cooling plant efficiency  of 6.2 COP.
  2. DES Path 2 – Full DES Performance Accounting:
    • Under this approach, the baseline system remains System 06 – Packaged VAV, without district cooling.
    • The proposed case is modeled with district cooling  network  with default DES COP value of 4.4 with 5% losses, as provided in LEED district cooling guideline.

Kindly confirm if the above interpretations and understanding for both DES Path 1 and DES Path 2 are correct, or advise if any revisions are required.

Thank you for your guidance.