FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

DHW (Domestic Hot Water) as process load

It the project I'm modeling for LEED, the DHW is provided by several electric water heaters located in the the restroom zones. The modeling software is considering this as a stand alone base utility as it is not connecting to any plants. Should such DHW be considered as process load. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 11/14/2014 - 09:29

Yes. ASHRAE calls this "Service" hot water...see the end of App. G. LEED generally allows you to take credit for energy savings due to water reduction in the WE credit for the amount of water DHW reduction as well if you document it properly, but please check me on that.

Fri, 11/14/2014 - 09:45

Thanks for the reply. If it could be considered as process load, should it be entered in table 1.4.4 in the Other Process Equipment table. Thanks also for the advice of water reduction, but I'm not involved in WE credit. Thanks.

Fri, 11/14/2014 - 13:23

Point 11 of Table G3.1 specifies how DHW shall be considered. If the system is part of the new project, see paragraph b. Regards

Fri, 11/14/2014 - 14:50

Domestic or service hot water is a regulated component of 90.1, see chapter 7. Since it is regulated (addressed by the standard), it is not a process load. So it gets entered in the Service Water Heating tables (Table 1.4.5 in the new section 1.4 tables or Table 1.4.4. in the old section 1.4 tables). Projects can claim energy savings associated with reduced hot water demand from low flow fixtures.

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.