FAQs about EAp2 :

The project is built on a site with existing exterior lighting installed. How should this be accounted for?

Can mezzanines open to floors below be excluded from the energy model?

How do I provide a zip code for an international location?

For a project outside the U.S., how do I determine the climate zone?

For a project outside the U.S., how do I determine the Target Finder score?

Do hotel rooms need automatic light shut-off control?

How commonly are the 90.1 mandatory compliance forms submitted as part of EAp2/EAc1?

The Section 9 space-by-space method does not include residential space types. What should I use?

Can the Passive House Planning Package (PHPP) be used to energy model for LEED?

Is it acceptable to model a split-type AC with inverter technology compressor as a heat pump, like modeling VRF?

Can the Trace 700 'LEED Energy Performance Summary Report' by uploaded to LEED Online in lieu of the Section 1.4 tables spreadsheet?

A portion of our building envelope is historic. Can we exclude it from our model?

Which baseline HVAC system do I use if my building has no heating or air conditioning?

For an existing building, do I need to rotate the model?

Our project has a diesel backup generator. Should we include it in our energy model?

Our project has a large process load—75%. Despite our efforts to make an efficient HVAC design, the cost savings are minimal. What can we do to earn this prerequisite and be eligible for LEED certification? Is there any flexibility in how we model the p

Can SHGC be higher in the proposed than in the baseline model?

Our process load is higher than 25%. Do we have to justify that?

Do I need to justify the electrical and fuel rates I am using in my model?

Our local code references ASHRAE 90.1-2010. Should I use that for my documentation, or 90.1-2007?

View answers »

Forum discussion

NC-2009 EAp2:Minimum energy performance

Densely occupied spaces

Hi Markus, I'd like to ask you for your opinion and advice about applying these values following the case described below. In LEED glossary such spaces are determined as 25 people per 100 sq ft. When applying DCV however, this value is 40 per 1000 sq. ft. The confusion comes, because both ratios are called "Densely occupied space". When it concerns IEQp1, normally the reviewers are OK with 40 per 1000 ratio, but sometimes they say that because the ratio exceeds 25 per 1000, in such rooms there should be CO2 sensors. Normally these sensors are controlling DCV (which compiles to 40 per 1000 ratio). If there is no DCV, because of ratio of 30 per 1000 (example) and by applying CO2 sensors, what these sensors are going to control in such situation? Could you please advice what could be the explanation to reviewers when they are referring to comply to 25 per 1000 ratio. Should IEQp1 be revised to reflect it, although there is no DCV required or designed. Thanks.

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Fri, 08/21/2015 - 16:44

The issue of densely occupied does not impact EQp1. The 40/100 in spaces over 500 sf is the threshold in 90.1 for having to install DCV in the baseline model. Reviewers will often look to the EQp1 documentation to determine if there are spaces in the baseline model that would require DCV. The 25/1000 is used within EQc1 to determine if you need CO2 or airflow monitoring. The reviewer should only be commenting on this issue within EQc1 and not within EQp1. Again they could be looking to EQp1 to see if there are spaces that would require CO2 sensors.

Fri, 08/21/2015 - 16:55

* "40/1,000" 40/100 would be the building's elevator (which is technically the critical zone when performing EQp1 calculations) :)

Add new comment

To post a comment, you need to register for a LEEDuser Basic membership (free) or login to your existing profile.