Dear sir, according to G3.1.2.5 of 90.1, Minimum outdoor air ventilation rates shall be the same for the proposed and baseline building designs except that When modeling demand-control ventilation in the proposed design when its use is not required by Section6.4.3.8. Can I understand it like this: 1.if demand-control ventilation is designed in the proposed design,and its use is not required by Section6.4.3.8, Minimum outdoor air ventilation rates of the design model should be modeled as the actual design with DCV control and the baseline case should model according to the ashare 62.1 without DCV control. 2.if demand-control ventilation is designed in the proposed design,and its use is required by Section6.4.3.8, Minimum outdoor air ventilation rates of the design model should be modeled identically with the baseline.as the actual design with DCV 3.if demand-control ventilation is not designed in the proposed design,minimum outdoor air ventilation rates of the design model should be modeled identically with the baseline.as the actual design without DCV 3.