Do you have a definition for Ds(%)? ASHRAE 62.1 does not have such a variable. There is a D for diversity, which seems to be the inverse of this Ds based upon experimentation. Can anyone advise?
You rely on LEEDuser. Can we rely on you?
LEEDuser is supported by our premium members, not by advertisers.
Go premium for
Roger Chang
Principal, Energy and Engineering LeaderDLR Group | Westlake Reed Leskosky
LEEDuser Expert
398 thumbs up
November 30, 2012 - 12:08 pm
D is the same as Ds. The s is a subscript to represent diversity at the system level. D is described in Chapter 6 of ASHRAE 62.1.
Dylan Connelly
Mechanical EngineerIntegral Group
LEEDuser Expert
472 thumbs up
December 4, 2012 - 7:00 pm
Nena/Roger,
I think there is some confusion here. D is not the same as Ds.
D=Diversity. Either in regards to the population served by the system vs FTE or the sum of all your zone maximum supply quantities vs your system capacity.
Example:
Your office spaces has a ventilation design capacity of 50 people and your conference rooms have a design capacity of 50 people. But your FTE is only 50 people. Your population D=50%. This reduces your outdoor air intake requirements.
Ds=Percentage of total design airflow rate at conditioned analyzed.
Example.
You have a VAV system with a 50% turn down for heating mode. Ds = 50%. Ds is typically the turn down at the terminal (for the design condition). For a VAV system, it is typically between 30-50%. For a constant volume system, Ds=100%. A lower Ds will give you a lower Ev coefficient, resulting in higher OA intake requirements.
On LEEDOnline, go to the main page for IEQp1. Then on the right, under quick links is a link to "Credit Resources." Download the "62MZCalc" excel file. Although it may confuse you more, at least there are some directions and definitions in that file.