CS-2009 EAc1:Optimize Energy Performance

Defining the building type

Hi, I have a 6 floors/2000 m² nonresidential building, and I am not sure about the system it should be. Area or number of floors is more relevant when choosing a system? It could be system 2 or 6 if considering the area, but it would be system 8 if considering its 6 floors, what looks non sense to me! Another question, do underfloor and technical floors count? Thank you for your help!

0

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Mon, 02/18/2013 - 14:53

It cannot be system 2 because that is residential only. If more than 5 floors it is a system 8. Neither area or number of floors is more relevant that the other. Read each statement under building type in Table G3.1.1A and apply the one that fits your project. For a six story building the only statement that applies is the one on the bottom - "nonresidental and more than 5 floors". Underfloor air systems do not count. A technical floor would likely count.