defination occupied spaces vs. ASHRAE 2011 handbook

dear all,

Credit IEQc9 requires that all occupied spaces should meet the requirements of HVAC background noise and refers to 2011 ASHRAE handbook, chapter 48, table 1. This table gives the maximum HVAC background noise per space for different room types. What if the roomtypes given in my project do not match the room types given in table 1 of the 2011 ASHRAE handbook?

I could look for simularity between the given room types and the used roomtypes, but interpretation could be a risk.Who can help?

Thank you in advance.

Ydo

1

You rely on LEEDuser. Can we rely on you?

LEEDuser is supported by our premium members, not by advertisers.

Go premium for $15.95  »

Wed, 01/10/2018 - 02:33

Hi Ydo, I think using the next closest room type is a good strategy, but if you want to be 100% sure I think you may need to reach out to GBCI. You might get a response here if you tell us more about what room types are in your project, so that folks can weigh in on which ASHRAE room types they're most similar to.

Thu, 02/15/2018 - 22:39

I Agree with Trista, when filling out the acoustic performance calculator you have to select from a list of pre-defined rooms. It is logical to select the closest comparable space.

Fri, 02/16/2018 - 11:56

I think that the same question and answer procedure is to be followed as for ASHRAE. So, better to ask ASHRAE what happens in such case, and refer to ASHRAE in LEED submission documents...  